Based on experience of passing USCG COC Examination, what are most common observation?

13 Nov, 11:41

Nov. 13, 2020, 11:41 a.m.
KnowledgeBase's gravatar image



Answer:

Following areas are usually targeted by USCG inspectors:

Gas Detection - Sequential and Continuous

Observations:

  • Unfamiliar with operating/calibrating procedures

  • Recommended span gas not certified or unavailable

Emergency Shutdowns

Observations:

  • ESD valve close time from actuation-greater than 30 seconds

  • Painted fusible elements

MARVS - Maximum Allowable Relief Valve Settings

Observations:

  • No tampered, missing, painted over, or worn seals

  • No setting certification record

Deck Water Spray

Observations:

  • Obstructed nozzles

  • Insufficient water pressure

Electrical equipment (On deck in the gas dangerous zone)

Observations:

  • Broken or exposed wiring

  • Cracked lenses

  • Broken bonding cables